In what steps can the radiator valve regulate heat? And for the thermostat?

Options
13

Answers

  • So, if the tado valves modulate do we still need to balance the rads via the lock shield?

  • eezytiger
    Options

    @Chris_topher Not a simple question to answer. Firstly, I am a homeowner and not a heating engineer, but my experience of Tado for over a year has left me with the following opinion....

    I think it depends greatly on whether you allow all rooms to demand heat - i.e. all rooms connected to the zone controller. In this scenario I think you can (perhaps) leave things to Tado, without balancing. Any rooms which don't receive enough heat straight away, due to distance from the boiler on the pipe run, will eventually fill the gap as they force the boiler to fire when closer rooms have received enough heat and shut themselves off.

    But, if you have your system configured like mine (only one zc room and all other rooms independent), then I think balancing is very much still necessary. Otherwise, when your zc room has enough heat and turns the boiler off, it's game over for the rest. You need to balance the system in order to push water/heat beyond the zc room. Alternative is to make sure that your zc room is the last on the pipe run, so that when it does call for heat the earlier rooms can grab their piece of the action first.

    But....

    You also want to make sure that you keep return temps low (for a condensing boiler) so you don't want the flow taking short cuts through a wide open, unbalanced radiator and immediately sending toasty water straight back to the boiler. So, depending how things pan out if left to Tado, you might still want to tweak the balance for maximum efficiency.

    I do monitor return temps from each radiator and I do find balancing beneficial. Otherwise some radiators will definitely short circuit the water flow and lower boiler efficiency.

  • gary333
    Options

    Could I just ask how you monitor temperature output from your rads? I have tried balancing my system (using probes) but when i do eventually get a 12oC differential the valves are near enough closed down to a fraction of a turn (1/8th or so). However, this then leads to the radiators not heating up and staying near enough stone cold at cooler 35oC - 40oC flow temps as soon as i put the SRT's back on.

    I'm banging my head when it comes to balancing as I just can't seem to achieve anything. From the previous post it looks like my effort to balance is then wasted if it Tado SRT's restrict the flow even more.

  • eezytiger
    eezytiger ✭✭✭
    edited December 2022
    Options

    @gary333 I have a whole bunch of these....

    https://www.amazon.co.uk/gp/product/B07ZN3QTBV/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1

    Enough for flow and return on all radiators at once, plus boiler flow and return as well.

    The two larger monitors log temps 24x7 in one minute (configurable) intervals. The smaller ones are real time monitors without logging. These are the ones that go on the rads.

    I then snugly secure each thermocouple with a Velcro strap, pressing it firmly against the copper pipe and insulating it from cooler air around.

    https://www.amazon.co.uk/gp/product/B001RPWPQE/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1

    I would not strive for Delta T 11 or 12 across each radiator. This will be easier to achieve with high flow temps (like 70C) because the rads will be emitting heat at a higher rate, thus losing it faster. It is a bold ambition for flow temps of 50C or less, especially if the house is already warm. Balancing the traditional way needs a cold house and a cold system to be done correctly. Once things warm up it is increasingly difficult to achieve these Delta T targets.

    The same thing goes for targeting Delta T 20C at the boiler. With a non condensing boiler and flow temps of 70+ this is again quite easy, for the same reasons. High temps lose heat fast.

    When you run the system longer and lower it is unreasonable to expect such huge temperature gradients. Further, if your boiler is range rated to low output, it is even more impossible.

    If I run my boiler without range rating then I can see those 20C deltas at the boiler. But range rated down to 9 kW instead of max 24 kW the water doesn't heat fast enough to create such extremes. I'm happy to see 8-9C delta at the boiler. Properly balanced, it is more likely that it'll be nearer to that for each rad as well.

    The way I balance, with a live running system, and a warm house, is to compare return temps from each rad with the return temp at the boiler, and also between rads. If any radiator return is hotter than the rest I squeeze the lockshield down just a little more on that rad.

    It's definitely not the conventional way of doing things, but it seems to work. Of course, it is far easier to do it my way when every radiator has a monitor attached at once. I can just run around glancing at the numbers without having to detach and reattach a single gauge and wait for equilibrium.

  • @eezytiger

    that is interesting, I’m running just the Tado trv’s on 10 rads and using vsmart with its wireless thermometer to fire the boiler and set hotwater tank recharge.

    So all my rads can call for heat but the boiler won’t do anything till vsmart says go.

    i did have it all integrated with the extension kit firing the boiler (I have the correct Vaillent module as had vrc470 before vsmart) but had issues with it not modulating, not heating the tank, or constantly heating the tank with no heating the house & Tado support would do stuff but not explain what they did leading to some days with no heating or hot water in winter which wasn’t fun with a baby in the house.

  • gary333
    gary333 ✭✭✭
    edited December 2022
    Options

    @eezytiger Thanks for that information. What you are saying about balancing makes sense, and explains why I can't ever seem to get more than a 5oC delta across the heating system). A Tomkat Gas training video on Youtube was showing the same issue you talk about (being impossible to balance using conventional wisdom. He by the end was doing something similar by just getting the rads to heat to the same temp when measured in the centre of the rad.

  • eezytiger
    Options

    @gary333 Ah, yes, I enjoy the Tomkat videos. That guy talks sense.

  • StavrosK
    Options

    Hi, just saw this thread.

    Doesn't the increased firing/stop cycles prematurely age the boiler?

    A boiler, and it's constituent parts, have an MTBF that cumulatively set an MTBF for the boiler in terms of number of firing cycles (affected by lots of other factors, to be sure) but nevertheless, doesn't the TADO controller increasing the number of firing cycles 5 fold equate to reducing the MTBF of the boiler by 80%?

    And if the boiler is an older mode, and is more fragile, increase the chance of failure sooner rather than later?

  • Valaki1234
    Options
    How do you interpret when a TRV calls 1% or 2% heat ?
    What is that supposed to mean ? Such low values…
  • Chapstar37
    Options
    Why not test it using a flow gauge, on the lock shield end.. Reduced flow = reduced aperture, increased flow = increased aperture, no flow = bypassed state
  • yes - but that does not answer the question - that just tells, that you are happy to be back in Deutschland /with a german product

  • roycruse
    roycruse
    edited November 2023
    Options

    Incrementally opening the radiator valves achieves nothing that on off control in a timely way cant achieve and comes with the added benefit of a mortised pin that can easily detect the entire range of movement and then calibrate its self for open and closed positions.

    if you just need a small amount of heat then open the rad valve for 2 minutes out of every 15 for instance. This works just the same as being open 13% of the way all the time....

    The thermal mass of a radiator full of hot water will mean you would not be able to tell the difference in the real world between a radiator modulated in the time domain rather than in the "percentage on" domain anyway.

    My valves for example are Danfoss and the total movement of the pin from fully out to all the way in is about 4-5 mm - I'm 100% sure there is not intended to be any partial opening of this valve and the standard TRV head would have quickly transitioned from open to closed and vice versa at the set temperature point.

    The end result is a system that can work with any manufacturer of radiator valve and can easily modulate your radiators based on what it learns over time. I've noticed my heating getting much batter at eliminating over and undershoots of temp over the weeks I've been using it. my room temps are now kept within 0.5degC of my set temps in all 4 zones all the time.

    Anyone contemplating leaving the system because it doesn't open the valves part way is quite frankly an idiot and doesn't understand physics or maths.

    edit: the only argument I can think of for attempting to partially open a rad valve would be battery life of the smart valve itself as it wouldnt be going all the way from on to off and back each time - but seeing as you'd expect this partial opening to be constantly adjusting its self to match demand I recon this would be minimal anyway.

  • johnbur
    Options
    There are at least two (or three?) much more important reasons for leaving the system than if the valves open part way or not....
  • roycruse
    Options


    I'm interested in your reasons... Ive had my own set of issues too that have been really draining to work with support to try to resolve... That said the deep dive Ive gone into this system in order to resolve my issues has given me an elevated perspective on how Tado and my Boiler interact which has left me with an overall "Impressed" feeling about the system as a whole.

  • johnbur
    Options
    Total reliance on a stable Internet connection (no local schedules)
    Total reliance on Tado servers working (ditto)
    Range issues in larger properties for many.
    Tado was probably the best out there five years ago when I invested in it, but the same issues are still there, and Tado are clearly not going to fix them.
    There are better options out there now, so I never recommend Tado any more.
    Sold all my kit on eBay including 15 TRVs for more than I paid for them back then (very strange).
  • roycruse
    Options

    I can see how those would be issues for some people, I dont like the idea of it either but in real world terms I dont think it will affect me, my internet is only ever down if the power is down so no heating anyway... if the internet is down you just control your heating manually with the wall stats and/or rad valve dials.

    For me the benefits of multizone control over my opentherm combi boiler out weigh those negatives and also out weigh the issues I have been having with opentherm comms errors...

    half my home automation is dependent on the internet - ie everything I control with my voice etc so i guess heating being one more thing is not the end of the world for me

    can I ask what other systems you considered and what you have ended up using. I came from nest originally which worked fine but had no multi zone functions and i was getting tired of the mrs saying the bedroom was cold when she went up to the room. I was going to go with the Honeywell evohome stuff before choosing Tado, i also have a lot of experience with heatmiser and hive. Im always curious if theres a better solution out there that ticks all (or more of) my boxes.

  • johnbur
    Options
    Just wait till there is an Internet issue in the middle of the night, and you will wish for local control when you get grief for waking up to a cold house!
    Drayton Wiser looks to have similar benefits to Tado but without the issues. That is what I would have gone with if looking for a new equivalent.
    I'm not a typical user though - have gone with Sonoff TRVs and separate temperature sensors all controlled by home assistant. Early days, but working well for me. I found that putting an external weather compensation sensor on the Ideal system boiler gives much better results than opentherm, so I've gone back to relay control.
  • johnbur
    Options
    What a coincidence!

    degraded performance affecting the tado° app
    New incident: Identified
    We have identified an incident affecting the performance of our app. Please subscribe to our status page for further updates and information on possible self-help.
    Time posted
    Nov 9, 21:11 CET

    Components affected
    Major Outage IoT cloud hub
    Operational Smart schedule execution
  • srichards
    Options

    Having had a tado system for a long time it seems there is a hierarchy of how much the radiators will open depending on set up.

    STRV only and can call for heat - the least amount of opening and undershoots/cold radiators a lot.

    STRV only independent - bit more, less undershoot.

    STRV + thermostat and can call for heat - bit more again and can be over or under depending on mood.

    STRV + thermostat and independent - more open more of the time so actually heating the fastest but more overshoot but tweaking temperatures can lead to a better compromise. The wall sensors allow 0.1C steps, STRVS only 0.5.

    It doesn't seem to learn from previous days. I think it might just about learn from first heating of the day as it's usually massive over shoot. Cool down then it keeps to temperature for the rest of the day if it's flat temperature reasonably well so it can do it right for small adjustments.


    I've set early start off and have a fixed temperature gradient schedule start so it can't start more than an hour before getting up. It's usually reasonable by then anyway. Early start would often be starting 2 hours earlier or more to have overshot massively by getting up time. This way it overshoots later in the morning so saves about an hour of heating.

  • 281HR
    Options
    What do you mean by fixed the temperature gradient? I assume you mean choosing one of the supplied options between OFF and Comfort. If so you have done nothing except used the App as intended.
  • Pythagoras
    Options

    anyone with functional hearing can tell that it's not just open and closed.

    Sometimes you hear a small adjustment, and if the Schedule changes, you will hear a larger adjustment

  • SteveIreland
    Options

    I'm reading a lot of posts about local control.

    I read that the V3+ stores Smart Schedules locally, so any loss of internet, the system will follow the schedule:

    "Depending on your region and specific hardware revision, your tado° V3+ Smart Thermostats store heating schedules locally, meaning they will continue to follow your Smart Schedule, even if the network connection is lost. The rollout of this feature is ongoing."

    As this appears to be relatively new, I thought I would post it here.

    Of course its still possible to override the Smart Schedule locally too, via the devices themselves, no?

    https://support.tado.com/en/articles/3477781-what-happens-when-the-internet-connection-is-temporarily-lost-can-i-still-control-my-heating-or-air-conditioning-using-tado

  • cbd20
    cbd20 ✭✭✭
    Options
    @SteveIreland Interesting, as that help page has definitely been updated as it didn't used to say that.

    My understanding was that the V3+ could not store schedule offline. However that help page definitely suggests that CERTAIN devices can or will do shortly ("the rollout of this feature is ongoing").

    I'm going to reach out to tado early next week to try and get an answer to this.
  • SteveIreland
    edited May 4
    Options

    @GrayDav4276 Please don't have a go at me. Just to be clear, I am quoting from the Tado Support pages, its not something I made up.

    I'm new to this so I am researching. They seem to suggest it is on the way, but if you feel I am somehow overstepping my boundaries, then sorry.

  • cbd20
    cbd20 ✭✭✭
    Options
  • royi
    royi ✭✭
    Options

    This is very interesting and will become a deal breaker if they do implement this. Unsure what they mean about the region.

  • SteveIreland
    Options

    @GrayDav4276 No worries.

    It does appear maybe Tado have listened to the VOX POP and have begun implementing a locally stored schedule. It was reading this that stopped me returning the lot as I am rural and work off 4G mobile broadband and regularly suffer power outages. However, this update is a good sign and I hope when they say that its dependent on region and hardware type that my region is covered and that the V3+ is the required hardware.

    What I might do is shut down my modem and see if the schedule is still evident.