Boiler constantly on not turning off when temp reached

Options
Hello,

I have just set my Tado v3+ wireless system up to my baxi 105 he boiler and the problem I have is the central heating is constantly on.

I have capped the old thermostat as to the instructions and wired the receiver to the boiler as to the instructions. So currently I am running off my old timer system.

If I ask the Tado to heat the receiver clicks to turn central heating on but the boiler doesn’t respond.

Any help would be much appreciated
1
1 votes

Active · Last Updated

Comments

  • Sammy_J82
    Options
    I think you may need to link out the timer on the front of the boiler
  • Sammy_J82
    Options
    Or possibly leave the old timer on constant so it isn’t timed or off
  • Aar0n
    Options
    Thank you for the reply if I leave the old timer constantly on the central heating system is constantly on
  • Montage
    Montage ✭✭✭
    Options

    It’s not wired correctly.

  • Aar0n
    Options
    I have followed the combi boiler live linked
  • Sammy_J82
    Options
    So on the old timer you should see to black wires going in and then two wires coming out that goes into the timer . If you turn the power off . Disconnect the two wires going into the timer and put a link in . See if that works . Just means the old timer isn’t connected anymore
  • Aar0n
    Options
    I’ll give that a a go thank you
  • Aar0n
    Options
    All sorted turned out the receiver box was to close to the boiler which was interfering with the boiler