w.Intercom = i;Wiring Sanity Check — tado° Community

Wiring Sanity Check

Hi!

My house has two heating zones, upstairs and downstairs, and a combo boiler so there is no hot water control.

I'm replacing the existing in room thermostat with a Tado wired thermostat. The existing wiring looks like

I was going to wire the Tado wired thermostat as:

Old -> New

  • N -> P1
  • L -> COM
  • NO1 -> NO
  • Strip back the ground cable -> P2
  • Remove the bridge between L and COM

Does that sound sensible to the experts here?


Thanks for any help!

Answers

  • Have you received instructions from Tado through the app? That sounds reasonable but best to follow what it says.
  • The app just kept telling me the existing install was a programmer, therefore couldn't be replaced by the wired thermostat I'd bought. Whilst is strictly true, as what I had could control hot water / act as a programmer, it wasn't in my case - but the app refused to help me beyond that.

    I just held my breath and took the plunge, and all seems well, both thermostats controlling their respective zones happily!

    Hope this can help someone else in a new build with a Danfoss TPOne-M

  • Thanks for this - you are a legend.

    Successfully setup on my side using these instructions!!