Which wires to connect?
Comments
-
I probably should have mentioned that we are connected to District heating :)0
-
Assuming you are connecting a wired thermostat.
Hcom goes to COM
Hon goes to NO
If you need to make the yellow and green wires safe you can connect them to P1 and P2. These are just parking terminals and have not electrical connection.
1 -
So on the setup instructions it asks to label 3 wires but there is no NC wire do I not need to worry about it is that the green and yellow one?0
-
Yes, you can ignore NC. NO and NC are just opposite poles on the relay switch. When NO is live then NC will be off and vice-versa. NO and NC cannot both be live at the same time, nor can they both be off.
2