Wiring to danfoss - honeywell
Hey there. i am a little confused how am i supposed to wire this, and also what configuration code choose later on. The system i have is Danfoss district heating, but i assume it works on Honeywell t3 wired thermostat, which only turns on/off Danfoss. When it does i can hear click noise. I am enclosing a pic of danfoss wiring.
there is also brown and green/yellow wire in the box. i believe brown is not plugged to anything.
Thanks!
0
Answers
-
Suggest you contact Tado and ask them about the T3H110A thermostat programmer. It seems that the cables migrate like this:
- Port A to Tado COM
- Port B to Tado NO.
But please contact Tado support and check.
0