Struggling with the Last part of my install

Options

Hi all,

Previous setup

Split Level Thermostats/Controllers (Danfoss TP4000)

Ideal Logic Combi ES35

Installed

I have installed the v3+ wireless kit to replace the downstairs termostat

I have installed the Wired thermo upstairs.

The Issue

The heating upstairs is working perfectly, I can control the boiler and temp from thermo or phone and hot water is pumping around the system.

The downstairs heating is causing a problem, I can control the boiler the same way as upstairs and the boiler kicks in to C when I demand the heating but the hot water does not circulate around the radiators.

However, the hot water does circulate if I connect the 2 wires from the now removed downstairs Danfoss controller.

I have checked the config on the receiver is set to combi

Receiver wiring

The downstairs wiring I connect for the hot water to circulate

Boiler Wiring (The com and chNO ports have the new wring for the receiver and the wires from the previous setup.) I assume this is where the problem is but not sure how to resolve.


Comments

  • hugbilly
    hugbilly ✭✭✭
    Options

    I think you need to bridge Live to CH Com in the wireless receiver . . .