Hot water control not working
Anyone have any ideas why the HW control isn't working?
Comments
-
Do you hear the relay click in the wireless receiver when you turn on HW?
If you do, double check the wiring as it may just be a bad connection.
Was it working 100% before the Tado install?
0 -
Hi,
No HW relay click or LED lit.
HW was working fine on the timer beforehand. For now (just so we have hot water) I've bypassed the receiver and permanently connected the 'HW on' line to mains live. Just means the boiler comes on whenever the HW tank stat switches to 'call', including at 3am...0 -
Sounds like either a configuration issue or faulty receiver
Since the LED doesn't come on, I suspect it's configuration so would reconnect you get tado support to check your system0 -
Ok thanks. I was thinking that's probably going to be my next course of action.0
-
I used the Tado chat on their website. They told me my thermostat had the wrong communication type and should now be fixed (it isn't) but I wonder if they somehow messed up the setting on whether the stat should be calling for the boiler on the nc/no contacts vs the analogue/digital communication pins.
0 -
I would think if they've done that, it would also stop your heating from working. I assume that's still OK?
Does the LED now come on when you select HW? If so, is there an audible click from the relay? If yes to both then you're next step is to double check wiring for the HW side of the system. If it's still not clicking or lighting the LED then I would go back to Tado support
0