Heating issue
I have set up a tado unit with trv on rads
In my lounge I have two rads one is fitted with trv and the other is the rad with no trv fitted as per central heating install. The problem is the room get very hot as the rad with out trv never shuts off as other rooms asking for heat any way I can sort this
In my lounge I have two rads one is fitted with trv and the other is the rad with no trv fitted as per central heating install. The problem is the room get very hot as the rad with out trv never shuts off as other rooms asking for heat any way I can sort this
0
Comments
-
You could try closing down the lockshield valve on the other rad with no TRV to reduce its heat output. Assuming of course that this rad is not being used as a bypass for the boiler overrun.
0 -
Do you mean Tado smart trvs? If so you should put them on all the radiators in the room, they don’t work like dumb trvs where there’s a conflict with the thermostat.0
-
Yes that’s what I mean the issue is that that one rad should have no trv and this is the one in the lounge which if the tado trv ask for heat the lounge rad get anyway0
-
Why do you think one radiator should have no trv? Do you mean as a bypass? If so, better to do that in a room with no Tado devices. Sounds like your problem will be solved if you put Tado trvs on all your lounge rads.0