w.Intercom = i;Danfloss Set2e Wiring — tado° Community

Danfloss Set2e Wiring

Hi all,

I am attempting to replace my Danfloss SET2E with a Tado wireless receiver.

Most of the wires I can identify to the corresponding terminals in the Tado wireless receiver.  

I can see that I have 2 bridges (L, 2 & 5), however I am not sure what my existing 1 and 4 terminals correspond to or are equivalent to NC or NO terminals in the Tado wireless receiver.

Is a Danfloss 'On' the equivalent of a Tado 'NC'?

Can anyone help?


Comments

  • Seems like when water c.q. heating is 'off' the common terminal is disconnected from the 'on' terminal. So this would mean you put the 'on' wires on the 'Normally Open' connectors.
  • @luteijn is correct. On is NO. Looks you have an s plan hot water system - you can probably follow the standard wiring linked below (section 4).

    https://cdn.brandfolder.io/607DGEMS/as/tqh86npbjjhws5gwkxfncbfh/104172-DIGITAL-WRP01IB01-INSTALLER_MANUAL-TA-UK-00-V2.pdf