Hi,
via App, how I can adjust the Viessmann Boielr Heating curve ?
F
0
Best Answers
-
@franny
You can't adjust the boiler heating curve parameters via the tado°App
You will need to contact your Viessmann engineer1 -
@franny i suspect you might need a viessmann controller to do that (or possibly an app?)0
Answers
-
thank you for swift reply .
0 -
The boiler heating curve can’t be adjusted by Tado app. You only can control heating curves when a outside temperature sensor is connected to your boiler and no thermostat is connected.-1
-
Dear Aligras, is partially correct.
fine and understand the Heating curve can't be adjusted by Tado App,
and is also correct to say heating curve is controlled when a temperature sensor outdoor is correct.
BUT
an internal thermostat can also be connected and then the temperature is modulated by the curve to reach the Internal setpoint (with hight flow rate if the curve is top one, and with minimal flow rate if is selected the bottom curve )
0 -
Yes, Franny!
It will work with an on/off thermostat but not with an opentherm thermostat.0 -