tado c/h causing my baxi 105e boiler to go into fault after every heating cycle
have contacted support , completely ignored the issue ,
after a heating cycle tado causes my boiler to go into fault ,ignition ,
if i reset it will go into another cycle ,and go back into fault ,
if i switch to hot water only , no issues ,tado is not controlling the hot water ,
but if i again go to heating and hot water ,a cycle of heating and we're in fault ,
i've set the target temperature down , so tado has not called for heat ,
guess what, no faults
had Lightwave rf for 6ish yrs before and never had this issue
after contacting support ,and showing the wiring ,
the response was ,Tado is not controlling the hot water, the problem lies elsewhere ?1
anyone else experienced this ?
Comments
-
This sounds like the boiler is complaining about an overheating cycle. That may be an issue with the bypass.
1 -
Are you sure you’ve got it wired up correctly?0
-
wired correctly ,if not i may have to give up my job as a sparks
0 -
Hmmm. What's the make of boiler and is it showing a specific fault code? If you've got the facility to wire it Opentherm/ebus you could try that, see if it makes a difference.
0 -
sorry just saw you put the make in the title. Doesn't look like it's opentherm/ebus compatible either. You could try resetting the extension kit, or check the contacts. That's all I got I'm afraid.
1 -
still working with support ,
gone through the resetting of boiler and wireless receiver ,
works on call for heat ,so all wiring is fine ,even used ferrules in terminals ,
and labeled sl and live ,showing pics ,proving continuity,
last request was what happens if you don't reset the boiler ?,
well it doesn't work !🤦♂️
0 -
So it’s not the wiring and it’s not the contacts, and it’s not the boiler because it worked with your previous system. I think that leaves two possible answers: 1. All Tado units are not compatible with your model of baxi. 2. Your specific Tado box has a fault that Tado in Germany can’t see.
Option two would be cheaper to rectify, though annoying as you’ve already shelled out for the kit.0 -
after 20 or so emails ,
i'm trying to get support to choose one of these options ,
and just take back the 8 x trvs and starter set ,
and i will go to a different system ,
lightwave worked fine on the boiler
0 -
@vespasmurf how many radiators do you have without a TRV fitted?0
-
one in the bathroom / towelrail
0 -
i take it you mean smart trv
0 -
I mean without any type of TRV. The most likely explanation for the lockout is insufficient flow of water in the CH circuit causing a safety sensor to trigger. You can check this by having one radiator where the manual valves at either end are fully open. Or remove some of the smart TRVs.
0 -
all smart except the towel rail which is standard trv set to 2/3 ,
but all was working with the Lghtwave rf heating control and smart trv's for a few yrs previously
0 -
will check the other end valves though
0 -
Assuming it is an issue with flow through the radiator circuit. Perhaps the Lightwave TRVs were passing a small amount of water when closed. Or perhaps the Lightwave controller was opening a TRV before starting the boiler. Whereas Tado starts the boiler before opening a TRV.
0 -
so possibly a software issue
0 -
@GrilledCheese2, in my Tado experience, the TRV opens then the extension kit relay clicks to start the boiler
I do agree that it's likely a flow issue which should be easy to check with at least one radiator left fully open
0 -
as the towel rail is a standard valve ,and not controlled by the tado ,
would this scene be covered ?
have been given a load more checklists to do by support just haven't had the opportunity ,
saved mew a fortune on heating through not working though !
0 -
Have you tried fully opening the towel rail trv yet? If it’s not a smart trv then it’s effectively invisible to Tado.0
-
Just pop off a couple of TRV's so there's flow through the system then test it. I had an issue when I first fitted Tado TRVs that I didn't have enough flow and the boiler threw an error. In the end I left the towel rad and a corridor rad with no trvs and that solved my issue. I just rebalanced the system using lockshields on these two rads.
0