Hi

I'm trying to install the wireless receiver in replacement of a danfoss 9000. Regarding the wiring the instructions state to label the wires plugged in to terminals 2 and 3, however I don't have any plugged in there. I only have two plugged into 5 and 6? Can anyone help? I have photos but can't see how to add?


Thanks
Matt

Comments

  • GrilledCheese2
    Options

    Terminals 5 & 6 are for the remote temperature sensor - you won’t need these for the Tado system. You must have some wires in terminals 1 to 4 which are used to turn the heating and hot water on.

  • Diab2005
    Options
    Ah OK I did wonder if that's what they could be for. There were only wires in terminals 3 & 4? Is there a way I can send you a photo?
  • GrilledCheese2
    Options

    Wire 3 is for Hot Water On and wire 4 is for Heating On. Assuming there’s nothing unusual about your installation I would expect the instructions for labelling to be:

    • Label the wire in terminal 3 as HW NO.
    • Label the wire in terminal 4 as CH NO.

    These labels will match the terminal names on the new wireless receiver.

  • Diab2005
    Options
    Perfect thanks mate. I found a post somewhere else that supports that too as NC is not needed
  • Hi, I've got a Danfoss 9000 programmable timer.

    I have two Danfoss HPA2 zone valve actuators.

    im going to replace this with a wireless thermostat V3 with hot water control.

    the zone valve actuators have the auxiliary switches which are normally open but the valve is closed with a spring return function, so do I wire the receiver for NO or NC ? I'm guessing NO to correspond with the auxiliary switches, but want to be 100%